Sinumerik Alarm 25020 Axis %1 zero mark monitoring of active encoder
The position encoder pulses between 2 zero marker pulses are counted (hardware function). A check is made in the interpolation cycle grid (standard setting 4 ms) as to whether the encoder always issues the same number of pulses between the zero markers. As soon as a difference is registered in the 4 counter bits of lowest significance, an alarm is triggered! The alarm can be reprogrammed in the MD ALARM_REACTION_CHAN_NOREADY (channel not ready).
– Mode group not ready.
– Axes of this channel must be re-referenced.
Please inform the authorized personnel/service department. The differences can result from transmission errors, disturbances, encoder hardware faults or from the evaluation electronics in the encoder used for position control. The actual value branch must there- fore be checked: 1. Transmission path: Check the actual-value connector on the motor and on the FDD module for correct contacting, encoder cable for continuity, and also check for short-circuits or grounding (loose contact?). 2. Encoder pulses: Encoder power supply within the tolerance limits? 3. Evaluation electronics: Replace or reconfigure the drive module used. Monitoring can be switched off by setting machine data 36310 ENC_ZERO_MONITORING [n]=… N … encoder number: 1, 2) is set to 0.